(a) why is it important to maintamn high efficiency of operation and low values of voltage regulation for power transtormers (6)
(b) A 100 KVA transtormer has 400 turns on the primary and 80 turns on the secondary. The primary and secondary resistances are 0.3 Ω and 0.01 Ω respectively, and the corresponding leakage reactances are 1.1 Ω and 0.035 Ω respectively. The supply voltage is 2200 V. Calculate:
(i) The equivalent impedence referred to the primary circuit
(ii) The voitage regulation and secondary terminal voltage for full load having a power factor of (i) 0.8 lagging and (ii) 0.8 leading.