Exam Question

With respect to tankers describe:

(a) How a pump room is ventilated.

(b) How cargo tanks are ventilated.

(c) Cargo tank protection as per SOLAS 1974.

(d) Additional alarms provided for inert gas systems of the 'inert gas generator' type.

Reference Answer

(a) Tanker Pump Room Ventilation
Pump rooms on tankers are required to be mechanically ventilated . The ventilation system must be of the exhaust type and designed to prevent the accumulation of flammable vapors. To ensure this, the system needs to have a minimum capacity of 20 air changes per hour based on the gross volume of the space. The exhaust fans must be a non-sparking type , and the air ducts should be arranged to provide effective ventilation throughout the entire space. The discharge from the exhaust fans must be led to a safe location on the open deck.
(b) Cargo Tank Ventilation
Cargo tanks are ventilated to make them "gas free," which means removing flammable or toxic vapors. This can be achieved using portable fans or blowers . These fans must be constructed to prevent incendiary sparking, for example, if the impeller were to touch the casing. The fans must also have sufficient capacity and penetration to quickly gas-free the entire tank atmosphere.

Full answer on MeoMock — surveyor-grade reference answers for 7,000+ written exam questions.